Formal Interpretation
NFPA 10
Portable Fire Extinguishers
2010 Edition
Reference: 5.5.5 and 6.6.1
F.I. No.: 10-02-2
Background:
of cooking appliances that use combustible cooking media (vegetable or animal oils and fats) be
listed and labeled for Class K fires. Subsection 6.6.1 requires class K fire extinguishers be provided for
hazards where there is a potential for fires involving combustible cooking media (vegetable or animal
oils and fats). Based on these two requirements, there is confusion with regard to requiring class K
extinguishers for stove top cooking.
NFPA 10, subsection 5.5.5 requires that fire extinguishers be provided for the protection
Questions No. 1:
commercial fryers employing combustible cooking media (vegetable or animal oils and fats)?
Do subsections 5.5.5 and 6.6.1 require class K extinguishers to be installed for
Answer:
Yes
Questions No. 2:
griddle?
Do subsections 5.5.5 and 6.6.1 require class K extinguishers to be installed for a
Answer:
Yes
Questions No. 3:
stove top frying pan?
Do subsections 5.5.5 and 6.6.1 require class K extinguishers to be installed for a
Answer:
Yes
Issue Edition: 2002
Reference: 4.2.3 and 5.7.1
Issue Date: July 7, 2005
Effective Date: July 27, 2005